If your capillary line was partially clogged, the compressor would run hot, the condensing coils would be hotter than usual near the compressor, but cooler than normal away from the compressor. the freezer temperature would be warmer than usual, and the current draw of the compressor would be less than normal. These symptoms are not evident in your case.
It there was air contamination, the freezer would not get as cold as 20 below zero
Are you sure your freezer temp. is 20 below?? So...I don't agree with the Whirlpool statement period.
So.. only way to get this fixed is to get a pro. refrigeration guy in there to get the whole picture!!