I agree with Icehouse - where are getting this info?
Are you reading 24 VAC at the low voltage board (where the t-stat wires come into the unit). Is this a split system, package unit, or wall mount?
If you are getting 24 VAC, then it is most likely not the transformer - you can't get low voltage without first having high voltage (120/240/277 etc). If this is a split system or a package unit I would look at the contactor first. I have a had a few situations like this where it was a bad contactor. If you feel comfortable doing this you can manually energize the contactor to see if the unit runs fine when it is engaged (you may want to use an insulated screwdriver just in case). If you do manually energize the contactor and the unit turns on, then you have a problem with the low voltage coil and need a new contactor. |